ModBus with TRV00210

Anonymous
Anonymous
Hii there!

Im trying to connect and read data via the ModBus protokoll and thru a Westermoe EDW100 with Shnieder-electronics own
ModBus module TRV00210. They are talking with some Circuitbreakers Micrologic 5.2E.

I seem to have everything setup due to recommendations, but i still cant get it to work.

What im trying to find out is if there is any strings i have to put in the Citect INI or if there is some software i need to get to make it work. Or if im reading the data wrong.

Has anyone been in touch with this combination of hardware before. Any help is welcome.



Hagberg
Programmer
Browik Installation i Örebro AB

Parents
  • Hi Hagberg,

    If I understand correct, you use the TRV00210 as a RS485 Modbus RTU interface for your circuit breakers and then convert the Modbus signal to Modbus over TCP/IP using the EDW-100.

    Divide your problem in two steps:
    1. Modbus RTU-communication
    2. Conversion to TCP/IP

    1. According to the documentation that I can find, the TRV00210 uses a RS485 interface, so try to communicate with the TRV00210 using another RS485 capable Modbus RTU device. Be aware of the following:
    - The TRV00210 uses 8N2 serial protocol format out of the box, not 8N1
    - Don't forget to use the Modbus station address you set with the rotary switches on the TRV00210

    2. When the Modbus RTU communication is working OK, then consider 3 options for TCP/IP conversion using the EDW-100:
    a. The EDW-100 acts as a TCP server
    Setup the EDW-100 in "TCP Server" mode.
    Citect uses the MODBUS driver and connects to the EDW-100 in TCP-mode (set -T option in Citect port special options). Please test if Citect can handle network interruptions longer than 30 seconds in TCP mode, because I had problems with that.

    b. The EDW-100 acts as a UDP server
    Citect uses the MODBUS driver and connects to the EDW-100 in UDP-mode (set -U option in Citect port special options). This is a reliable mode for the EDW-100 in combination with Citect using various serial protocols over TCP/IP. Citect recovers from network interruptions fine in UDP mode.

    c. The EDW-100 acts as a protocol converter (Modbus RTU -> Modbus TCP gateway)
    Set up the EDW-100 in "Gateway Server" mode and use Citect's MODNET driver or one of the variants.
    I have not tested this mode yet, so please report back any findings you have when testing this.

    In all cases the Citect drivers handle the TCP/IP packets themselves, so you don't have to install the virtual comm port software that comes with the EDW-100.
    Do not forget to set the Modbus station address in Citect's I/O Device form. This is NOT documented in the driver's help! The help says that you should leave the address field empty, but this is incorrect!

    Best regards,

    Patrick van Dijk
    CCSE v6.1 / v7



    imtechcsi
    CIP Gold
    Imtech Traffic & Infra B.V.

Reply
  • Hi Hagberg,

    If I understand correct, you use the TRV00210 as a RS485 Modbus RTU interface for your circuit breakers and then convert the Modbus signal to Modbus over TCP/IP using the EDW-100.

    Divide your problem in two steps:
    1. Modbus RTU-communication
    2. Conversion to TCP/IP

    1. According to the documentation that I can find, the TRV00210 uses a RS485 interface, so try to communicate with the TRV00210 using another RS485 capable Modbus RTU device. Be aware of the following:
    - The TRV00210 uses 8N2 serial protocol format out of the box, not 8N1
    - Don't forget to use the Modbus station address you set with the rotary switches on the TRV00210

    2. When the Modbus RTU communication is working OK, then consider 3 options for TCP/IP conversion using the EDW-100:
    a. The EDW-100 acts as a TCP server
    Setup the EDW-100 in "TCP Server" mode.
    Citect uses the MODBUS driver and connects to the EDW-100 in TCP-mode (set -T option in Citect port special options). Please test if Citect can handle network interruptions longer than 30 seconds in TCP mode, because I had problems with that.

    b. The EDW-100 acts as a UDP server
    Citect uses the MODBUS driver and connects to the EDW-100 in UDP-mode (set -U option in Citect port special options). This is a reliable mode for the EDW-100 in combination with Citect using various serial protocols over TCP/IP. Citect recovers from network interruptions fine in UDP mode.

    c. The EDW-100 acts as a protocol converter (Modbus RTU -> Modbus TCP gateway)
    Set up the EDW-100 in "Gateway Server" mode and use Citect's MODNET driver or one of the variants.
    I have not tested this mode yet, so please report back any findings you have when testing this.

    In all cases the Citect drivers handle the TCP/IP packets themselves, so you don't have to install the virtual comm port software that comes with the EDW-100.
    Do not forget to set the Modbus station address in Citect's I/O Device form. This is NOT documented in the driver's help! The help says that you should leave the address field empty, but this is incorrect!

    Best regards,

    Patrick van Dijk
    CCSE v6.1 / v7



    imtechcsi
    CIP Gold
    Imtech Traffic & Infra B.V.

Children