The recommended architecture for the PI System when collecting PMU data is different from our standards. This is because the high speed data coming from PMUs, FFT and other analysis can quickly fill up the archives at a much faster rate than a standard SCADA system. Usually, a WAMS PI System will be designed in such a way that it has enough disk space to hold a pre-defined amount (and minimum) of history for the PMU readings and will start cycling through the old archives as they fill up.
In other words, the SCADA data tags would be affected negatively if it was in the same PI Server as the PMU tags by having a limited amount of history available and potentially slow retrieval rates by client tools.
With that said, the overall architecture will have the standard PI System components plus potentially the separate servers for hosting PMU and FFT data as shown below:

Ps: This is the reason for the PI C37.118 interface to require a CoE approval before a new download.